Grounding Electrode Conductor - NEC Section 250 Definition

By Pablo Diaz, P.Eng, Grounding Systems Technologies (GST)

Grounding Electrode Conductor

Section 250.4(A)(1) of the National Electrical Code (NEC) states that the electrical system is connected to ground to limit voltage imposed from lightning strikes, line surges, high-voltage crossovers and to stabilize voltage-to-ground under normal operation.

Visit our Grounding and Bonding and The NEC - Section 250 Course

The equipment is then connected to the system to limit voltage-to-ground at the equipment. This is done through a branch circuit conductor that extends the connection from the equipment to the “Grounding Electrode Conductor”, back at either the service or the source of a separately derived system. This ensures control of the voltage to prevent physical damage to electrical equipment.

NEC requires that, where available on the premises at each building or structure served, all grounding electrodes including “made” electrodes be bonded together to form the “Grounding Electrode System”.

 

Visit our Electrical Grounding Training Page

The “Grounding Electrode System” includes metal underground water pipes, metal frames of buildings, concrete-encased electrodes and ground rings.

The general requirement is that a bonding jumper must be installed between the grounding electrodes to bond them together.

  • “Grounding Electrode Conductor is run from the service equipment to one of the grounding electrodes that are bonded together.
  • NEC Section 250-24(c), is a requirement to connect the equipment grounding conductors, the service-equipment enclosures, and where the system is grounded, the grounded service conductor to a grounding electrode. The conductor used to make this connection is the “Grounding Electrode Conductor”.
  • “Grounding Electrode Conductor” (GEC) from an electrical service to a ground rod, pipe or plate electrode is never required to be larger than 6 AWG copper or 4 AWG aluminum unless the GEC continues on from the rod, pipe or plate to connect another electrode that may require a larger GEC such as a concrete encased electrode building steel or metal underground water pipe that qualifies as a grounding electrode.

The requirements of NEC Section 250.2 states that an effective ground fault current path is an intentionally constructed, permanent, low impedance, electrically conductive path designed and intended to carry current under a ground fault conditions from the point of a ground fault (like an overcurrent device) on a wiring system to the electrical supply source and that facilitated the operation of the overcurrent protective device. This is the function of a “Bonding Conductor” and not the function of a “Grounding Electrode Conductor”.

With that assumption, and based on that incorrect interpretation, many electricians assume that in a properly functioning electrical system, currents in grounding electrode conductors are only present during faults, and only for a very short time.

Although further examination of 250.4 (A)(5) should make it clear that the earth shall not be considered an effective ground fault current path, misconceptions still persists.

  • “Grounding Electrode Conductor” (GEC) from an electrical service to a ground rod, metal water pipe or plate is never required to be larger than 6 AWG copper.
  • Aluminum “Grounding Electrode Conductors” can not be in contact with earth, masonry or subjected to corrosive conditions.
  • ”Grounding Electrode Conductor” is permitted to “supply” or “serve” any number of grounding electrodes, but must be sized for the largest grounding electrode conductor required.

TRAINING EF COURSES

Top