Understanding The Arc Flash Boundary Chart

By R.W. Hurst, Editor

arc flash boundary chart

An arc flash boundary chart is an essential tool for electrical workers and safety professionals to ensure that workers are adequately protected from the hazards of arc flash incidents. The arc flash boundary is the minimum safe distance from energized electrical equipment, and it's critical to accurately calculate the arc flash boundary for each piece of equipment.

Visit Our CSA Z462 Arc Flash Training Page

Visit Our NFPA 70E Arc Flash Training Page

The NFPA 70E and CSA Z462 standards provide guidance on the arc flash boundary and how to calculate it. It's essential to follow these standards and provide specialized training to qualified workers to ensure that they know the hazards and how to work safely around energized electrical equipment.

Implementing an effective arc flash safety program that includes accurate arc flash boundary calculations, appropriate PPE, and specialized training for workers is critical to protect workers from the hazards of arc flash incidents.


What is an Arc Flash Boundary?

An arc flash boundary is a designated area around energized electrical equipment where an arc flash could cause serious injury or death to a worker not wearing the appropriate personal protective equipment (PPE). The arc flash boundary is a critical component of electrical safety programs, as it helps to identify potential danger areas and ensure that workers are aware of the hazards.

Arc flash boundaries are established based on the incident energy that could be released during an arc flash. Incident energy is the thermal energy that could be released during an arc flash, measured in calories per square centimetre (cal/cm²). The higher the incident energy, the greater the potential for injury and the larger the arc flash boundary.


What are Arc Flash Boundaries?

The arc flash boundary is the minimum safe distance from the energized equipment that an unqualified worker can approach without wearing PPE. The NFPA 70E and CSA Z462 standards provide guidance on the minimum distances that should be maintained between energized electrical equipment and workers based on the incident energy levels.

There are three arc flash boundaries that are defined by the NFPA 70E and CSA Z462 standards:

Limited Approach Boundary (LAB) - The limited approach boundary is the minimum distance from the energized equipment that an unqualified person can approach. This boundary is generally marked with a yellow boundary line and is intended to keep unqualified personnel from entering the hazard zone.

Restricted Approach Boundary (RAB) - The restricted approach boundary is the minimum distance from the energized equipment a qualified worker can approach without wearing the appropriate PPE. This boundary is marked with a red boundary line and indicates the point where a worker must begin wearing the appropriate PPE to prevent injury.

Prohibited Approach Boundary (PAB) - The prohibited approach boundary is the closest distance to the energized equipment considered safe for any person to approach, regardless of PPE. This boundary is marked with a black boundary line and is used to indicate the most hazardous area.


What is the Minimum Arc Flash Boundary?

The minimum arc flash boundary is determined by the incident energy level that could be released in the event of an arc flash. The incident energy level is calculated using complex mathematical formulas that consider the system voltage, available fault current, and the time the protective devices take to clear the fault.

The NFPA 70E and CSA Z462 standards provide tables and formulas to help calculate the incident energy and the minimum arc flash boundary distance. The minimum arc flash boundary is the distance from the energized equipment where the incident energy is below 1.2 cal/cm², which is the level of thermal energy that can cause second-degree burns to unprotected skin.


What is the Arc Flash Boundary for 480V?

The arc flash boundary for 480V equipment can vary depending on the incident energy level. However, the NFPA 70E and CSA Z462 standards provide a table that specifies the minimum arc flash boundary for 480V equipment based on the available fault current and the protective device clearing time.

For example, if the available fault current is 10,000A and the protective device clearing time is 0.1 seconds, the minimum arc flash boundary for 480V equipment is 3 feet for a category 1 PPE level.

It's important to note that the arc flash boundary distance can vary depending on several factors, including system voltage, available fault current, and protective device settings. Therefore, it's essential to accurately calculate the arc flash boundary for each piece of equipment to ensure that workers are adequately protected.


How to Calculate Arc Flash Boundaries?

Calculating the arc flash boundary requires an understanding of the electrical system and the potential hazards associated with it. The process involves a detailed analysis of the electrical system and the potential fault currents that could occur.

The NFPA 70E and CSA Z462 standards provide guidance on calculating the arc flash boundary using various methods, including the incident energy analysis method and the arc flash PPE category method.

The incident energy analysis method involves performing a detailed electrical system analysis to determine the potential incident energy levels at different points in the system. This method requires complex calculations and detailed information about the system components, such as the available fault current and protective device settings.

Based on the incident energy level, the arc flash PPE category method determines the minimum PPE level required for a specific task. This method involves using tables to identify the required PPE level for a specific incident energy level and selecting the appropriate PPE based on the task.

Regardless of the method used, ensuring that the arc flash boundary is accurately calculated is critical to provide adequate worker protection.


Can an Unqualified Person Cross the Arc Flash Boundary?

An unqualified person should never cross the limited approach boundary of an energized piece of electrical equipment. The limited approach boundary is the minimum distance from the energized equipment that an unqualified person can approach, and it's intended to keep unqualified personnel from entering the hazard zone.

Only qualified workers who have received specialized training and are authorized to work on or near energized electrical equipment should cross the restricted approach boundary. Crossing the restricted approach boundary without appropriate PPE is dangerous and can result in severe burns, injuries, or even death.

Related Articles
TRAINING EF COURSES

Top